I have a burnham boiler about 4 year sold a V8-3

It keeps building up pressure ; I let out a littel water to reduce pressure and it builds up again quickly/ over 22
Got any ideas

thanks\\

JIm
Reply New Topic
  #47536 Posted 11 Months, 2 Weeks ago
Jeffie
Admin
Posts: 1336
graph
User Offline
 
Jim welcome to the forum It sounds like there is a problem with the pressure vessel. To be on the safe side you better call in a professional with this kind of jobs.
Reply New Topic
  #47589 Posted 11 Months, 1 Week ago
Tieger plumbing
Junior Boarder
Posts: 32
graphgraph
User Offline
 
1- check the automatic fill valve (SET between 12 -15 PSI)

Check the expansion tank make sure it is not water logged, Check the tank less coil if applicable.

22 PSI is NOT excessive as it depends on the static head of YOUR system