I have a burnham boiler about 4 year sold a V8-3

It keeps building up pressure ; I let out a littel water to reduce pressure and it builds up again quickly/ over 22
Got any ideas

thanks\\

JIm
Administrator
Administrator
Jeffie
Blog Posts: 0
Forum Posts: 1349
Rating: 17ApplaudCriticize
Posted 1 Year, 3 Months ago #2
Jim welcome to the forum It sounds like there is a problem with the pressure vessel. To be on the safe side you better call in a professional with this kind of jobs.
Tieger plumbing
Junior Boarder
Blog Posts: 0
Forum Posts: 33
Rating: 1ApplaudCriticize
Posted 1 Year, 3 Months ago #3
1- check the automatic fill valve (SET between 12 -15 PSI)

Check the expansion tank make sure it is not water logged, Check the tank less coil if applicable.

22 PSI is NOT excessive as it depends on the static head of YOUR system