Hi,

The Temperature Pressure Relief Valve on my 9 year old AO Smith water heater has started to drip. It only does this when we use our central air. Any ideas on why or what I should do about it? I am planning on replacing the valve tomorrow, but find it curious that it only leaks when the air is in. The water heater is about 4 feet from the furnace, which is what circulates the air. It's a forced hot air system. Any help will be appreciated.

Thanks,

tj
Reply New Topic
  #45962 Posted 1 Year, 4 Months ago
Jeffie
Admin
Posts: 1336
graph
User Offline
 
maybe the air is pressuring in some way while, if this is the case, possible debris contained in the valve will start the leaking. In a case like this it may help to open and close the valve a few times in order to try to get rid of the debris.
Reply New Topic
  #45989 Posted 1 Year, 3 Months ago
tjw61
Fresh Boarder
Posts: 2
graphgraph
User Offline
 
Thanks, it turns out it was the water heater expansion tank. It had blown and wasn't regulating the pressure correctly. After replacing it, it turned out the Temperature Pressure Relief Valve wouldn't reseat and it was replaced also. Turns out the AC thing was just bad timing!

Thanks again,

tj